PostPosted: Thu Aug 30, 2012 4:54 am    Post subject: Charger needed to revive 18 aH Lead Acid Batteries Reply with quote

At 06:22 PM 8/29/2012, you wrote:

<rparigor(at)suffolk.lib.ny.us>

Hi Group

I have a task to try and revive some 18 aH 12 volt sealed AGM
batteries that weigh in at ~ 14.5 pounds.

The charger that was being used on them begins at a 3.5aH charger,
then slows down a bit and peaks ~ 14.2/3 then goes to 13.7 float.

After a while, I don't know if from letting discharge too much or for
too long, or the 3.5 aH is a bit too fast, but what happens is the
batteries although they peak and go to float, they really don't take
too much of a charge and have a very low capacity.

How long does the charger stay in a top-off mode? 3.5
amps charge is okay. But the absorption charge should
sustain at 14.7 or so until the charge acceptance current
of the battery is 100 mA or less.

http://tinyurl.com/9s7kpww

I have a 900mA Yuasa motorcycle charger, that does a little better.

Now what I did find works really well, is using the fool cheapest of
cheap battery chargers I gave away with the 9aH batteries I sold on
AeroElectric.

Do you have a way to measure and plot the performance
of your charger. Also a way to measure real capacity
as a result of that charging protocol? One of these
West Mountain Radio analyzers can be used to both plot
charger performance -AND- confirm the battery's acceptance
of charge.

That charger is nothing more than a 500mA transformer that supplies a
constant 500mA current, then the circuit just looks for 15.4/5 and
turns off. Now mind you it can take not hours, but days to reach that
magic 15.4/5 number, and some batteries can not be revived, but most
can. Then I found that if I take two of these batteries and parallel
them and let the poor 500mA charger reach 15.4/5, it gets about as
good as it gets so far.

Yes, the higher trip point is well into the range
recommended for absorption charging . . . perhaps
a bit high but certainly high enough.

I think that the longer elevated voltage is perhaps desulfating??

Don't know if it's a sulfation problem at all,
just a quirk of the chemistry. Those two batteries
I bought from you have been subjected to a couple
of charge/discharge cycles using just a Battery
Tender and they seem to be taking on a full load
of watt-seconds.

Just for grins, I'll do a cap-check on one and then
do a manual, constant current charge that guarantees
sufficient dwell at absorption voltages and repeat the
cap-check.

There's a number of exemplar smart-charger profiles at:

http://tinyurl.com/9t6t8x8

in particular, take a look at this curve plotted on
a Schumacher 1562A

http://tinyurl.com/945zdog

it seems to be doing the right things in accordance
with contemporary wisdom

The Battery Tender Jr has the right moves too,
but not as defined. That's what I use to charge
and maintain a stack of test batteries here in
my shop.

Battery Minders behaved like this when I
tested them

http://tinyurl.com/9paguuy

Little or no absorption dwell, very low end
of charge trip point. I used to have a couple
but after doing these tests, I relegated them
to maintaining a fully charged battery only.
Gave them away to family members for keep batteries
in garden tractors and seldom used vehicles topped
off . . . but cautioned against expectations for
getting the battery up to 100%. It would probably
pump it up to a value that would start the engine.
Once the lawn was mowed, the machine's normal recharging
protocols would probably top off the battery where
the Battery Minder would be useful for maintaining
that condition.

I have a constant current 2 aH charger, and if I let it go much over
14.4 the batteries make a minor bubbling noise that I don't like too
much and figure if I let it go it will begin venting? I let it go 2
hours but the 500mA charge brought back more capacity.

Sorry for the long winded explain, what I need:

I need a consistent source for a fairly inexpensive charger that can
help revive these batteries.

I looked at Walmart, they have a 1.5 amp charger that peaks too low.

Is this the 1562 or it's offspring? I'm surprised
that it wouldn't behave much as the version I
tested some years ago. Schumacher is the BigDaddy
of battery charging tools. If anyone should know
how to do it right, it should be them.

I'll do a looksee to find out if the Battery Tender
falls short of top-off when used as a stand-alone
charger-maintainer.

I thought the short answer to your question would
be to pick up a Schumacher 1562 or current
replacement at Walmart. Do you have one of these
in hand? You could mail it to me and I can run some
plots on it.
Bob . . .


- The Matronics AeroElectric-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?AeroElectric-List
Back to top
rparigoris



Joined: 24 Nov 2009
Posts: 805

PostPosted: Thu Aug 30, 2012 9:16 am    Post subject: Re: Charger needed to revive 18 aH Lead Acid Batteries Reply with quote

Hi Bob

Thx. for the reply.

The chargers being used are Chargetek 3 stage chargers:
http://www.chargetek.com/resources/battery-charger-basics/

I didn't measure it, but the link says it turns off at between 1/100C and 1/50C, so on a 17aH battery that is between 170 and 340mAs.

What is the amp draw that you need to drop below for the Schumacher 1562A to drop out of absorption rate and go to float with a 17aH battery?

If it's 100mAs or less that may just be the ticket to success.

Is there a way to adjust this point to allow it to stay in absorb for a longer time?

Thx.
Ron Parigoris


- The Matronics AeroElectric-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?AeroElectric-List
Back to top
View user's profile Send private message
nuckolls.bob(at)aeroelect
Guest





PostPosted: Thu Aug 30, 2012 12:32 pm    Post subject: Charger needed to revive 18 aH Lead Acid Batteries Reply with quote

At 12:16 PM 8/30/2012, you wrote:

<rparigor(at)suffolk.lib.ny.us>

Hi Bob

Thx. for the reply.

The chargers being used are Chargetek 3 stage chargers:
http://www.chargetek.com/resources/battery-charger-basics/

I didn't measure it, but the link says it turns off at between 1/100C
and 1/50C, so on a 17aH battery that is between 170 and 340mAs.
Hmmmm . . . okay. I seem to recall that Skip
Koss talked about recharge currents below 100
mA for terminating an absorption cycle on really
big batteries like the 30-50 a.h. aircraft batteries
we used at HBC. Kicking off that high seems a
bit 'light'.
What is the amp draw that you need to drop below for the Schumacher
1562A to drop out of absorption rate and go to float with a 17aH battery?

Have no idea. Never measured it. Don't know how
critical it is. Given that the Schumacher product
stayed in a absorption mode for a significant time
suggested that a righteous absorption charge was
being delivered. I don't have any 1562's around
to measure. I could put one of your Chargetek
machines on a DAS and find out where they are
calibrated.

If it's 100mAs or less that may just be the ticket to success.

Yes.

Just for grins, I took one of the 12a.h. batteries I
bought from you that has been on a Battery Tender
for the last several days (green light on, in maintenance
mode. Fooey, didn't read the float voltage first) and
hooked it to a 14.6v power supply. Charge current jumped
to 300mA and over the next 12 minutes it fell to 100mA.
Putting a crayon to the numbers suggests that the battery
is 12 a.h. x 12v x 3600 s/hr ~ 500,000 watt-seconds
at full charge. The little boost on the bench put in 200
mA average for 12 min for 0.2 x 14 x 720 ~ 2000 watt-seconds
or less than 0.5% of capacity. Hence I deduce (1) that the
Battery Tender did indeed return and support this battery
to 100% of rated capacity and (2) an end of absorption cycle
value of 100mA is not an unreasonable calibration point.

It would be interesting to plot an absorption cycle for
energy the battery takes on after recharge current drops
below 300mA . . . I'm guessing that it's probably less than
1% of rated capacity . . . but don't know without measuring.

Is there a way to adjust this point to allow it to stay in absorb for
a longer time?

Haven't had a 1562 (or replacement) apart to find out.
But even if the EOAC termination value is higher, I'm
not convinced that you're going to loose much. We could
set up the experiment and find out.
Bob . . .


- The Matronics AeroElectric-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?AeroElectric-List
Back to top
nuckolls.bob(at)aeroelect
Guest





PostPosted: Fri Aug 31, 2012 8:12 am    Post subject: Charger needed to revive 18 aH Lead Acid Batteries Reply with quote

At 06:22 PM 8/29/2012, you wrote:
Quote:

<rparigor(at)suffolk.lib.ny.us>

Hi Group

I have a task to try and revive some 18 aH 12 volt sealed AGM
batteries that weigh in at ~ 14.5 pounds.

The charger that was being used on them begins at a 3.5aH charger,
then slows down a bit and peaks ~ 14.2/3 then goes to 13.7 float.

Pursuing another train of thought: It is
possible that the batteries have suffered
so degradation of performance due to combinations
of age, conditions of storage, or even manufacturing
quality.

Skip Koss has related Concorde's techniques for
recovering what appears to be a totally trashed
battery. The process includes things like application
of 24v on a 12v battery until recharge currents
rise above some established value followed by
a couple deep charge/discharge cycles. He
said this process may well flog the horse back
to some demonstration of life . . . but you
never get back to 100% even if the battery
is young.

There's a mil-spec requirement for being able
to recover a badly discharged battery . . .
like a dead-short on it for a week before
the recovery process is applied. Capacity
tests measure proportion of chemistry still
active . . . and there are some failures that
cannot be recovered with outside stimulus.

Bob . . .
Quote:
After a while, I don't know if from letting discharge too much or
for too long, or the 3.5 aH is a bit too fast, but what happens is
the batteries although they peak and go to float, they really don't
take too much of a charge and have a very low capacity.

I have a 900mA Yuasa motorcycle charger, that does a little better.

Now what I did find works really well, is using the fool cheapest of
cheap battery chargers I gave away with the 9aH batteries I sold on
AeroElestric.

That charger is nothing more than a 500mA transformer that supplies
a constant 500mA current, then the circuit just looks for 15.4/5 and
turns off. Now mind you it can take not hours, but days to reach
that magic 15.4/5 number, and some batteries can not be revived, but
most can. Then I found that if I take two of these batteries and
parallel them and let the poor 500mA charger reach 15.4/5, it gets
about as good as it gets so far.

I think that the longer elevated voltage is perhaps desulfating??

I have a constant current 2 aH charger, and if I let it go much over
14.4 the batteries make a minor bubbling noise that I don't like too
much and figure if I let it go it will begin venting? I let it go 2
hours but the 500mA charge brought back more capacity.

Sorry for the long winded explain, what I need:

I need a consistent source for a fairly inexpensive charger that can
help revive these batteries.

I looked at Walmart, they have a 1.5 amp charger that peaks too low.

Any ideas?

Thanking you in advance
Ron Parigoris


Read this topic online here:

http://forums.matronics.com/viewtopic.php?p=382105#382105

-----
No virus found in this message.
Checked by AVG - www.avg.com


Bob . . .


- The Matronics AeroElectric-List Email Forum -
 

Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:

http://www.matronics.com/Navigator?AeroElectric-List
Back to top
Display posts from previous:   
Post new topic   Reply to topic    Matronics Email Lists Forum Index -> AeroElectric-List All times are GMT - 8 Hours
Page 1 of 1

 
Jump to:  
You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot vote in polls in this forum
You cannot attach files in this forum
You can download files in this forum