		nuckolls.bob(at)aeroelect Guest
 
 
 
 
 
  | 
		
			
				 Posted: Mon Sep 18, 2017 10:19 am    Post subject: GFCI Breaker keeps tripping (Non   Aviation) | 
				     | 
			 
			
				
  | 
			 
			
				At 06:39 PM 9/17/2017, you wrote:
   	  | Quote: | 	 		  --> AeroElectric-List message posted by: Charlie England <ceengland7(at)gmail.com>
 
  On 9/17/2017 4:20 AM, donjohnston wrote:
   	  | Quote: | 	 		  --> AeroElectric-List message posted by: "donjohnston" <don(at)velocity-xl.com>
    | 	 
  | 	  
   <snip>
 
  
   	  | Quote: | 	 		  | Having said all that, if I were getting random GFI trips with nothing on the circuit, I'd be looking for 'issues' with both the ground wiring and the neutral wiring. I'd probably start with the neutral, making sure that its 'bond' to the ground in the panel is secure . . . | 	  
 
    Wiring issues downstream of the GFI are certainly at the
    top of the list . . . and not hard to troubleshoot. A GFI
    is a specialized incarnation of the clamp-on, AC ammeters
    that are useful service tools. They let you measure current
    in a wire by detecting the magnetic field outside the wire.
    You can interpret current flow in the wire without having to
    break into it.
 
    The Hall Sensor devices common to DC current measurements
    function on a similar principal. Hall devices can measure
    both ac and dc currents, the familiar clamp-on service instruments
    are transformers GENERALLY limited to AC measurements.
    Measurements are made by running ONE wire in the supply
    loop through the instrument's measurement aperture.
 
    You could use such an instrument to detect wiring faults
    by running BOTH supply loop wires thorough the aperture.
 
  [img]cid:.0[/img]
 
    During normal operation, the current flowing in the outbound
    wire (hot) exactly equals the current on the return (neutral)
    wire. Snapping the ammeter over a properly operating power
    pair will show a net current reading of zero.
 
    Now, assuming there is some leakage current from hot to
    a remote ground, there will be an imbalance in the hot
    vs. neutral conductors. If this current exceeds something
    on the order of 5 MILLIAMPERES, the magnitude of leakage
    is considered hazardous.  Most service instruments are
    not sensitive enough to detect/measure leakage currents
    this small.
 
    A ground fault breaker is simply an ac ammeter built
    into the breaker housing. But in place of an observable
    display, the transformer drives electronic circuitry
    that (1) watches for imbalance in the hot/neutral
    pair exceeding 5ma and (2) unlatching the breaker's
    hold-closed mechanism when the leakage limit is exceeded.
 
    The illustration above shows how the leakage is
    monitored by passing both paths through the same
    aperture.  Making this happen in a GFI breaker
    requires that both the hot and neutral wires pass
    through the breaker. 
 
  [img]cid:.1[/img]
 
    This illustration shows that instead of taking
    the neutral wire right to the panel ground bus, it
    goes to a terminal on the breaker. So not only
    will this breaker have TWO terminals for house
    wiring, a 'pigtail' routed the panel ground bus
    completes the neutral path.
 
    It's unlikely that nuisance tripping is caused
    by loose connections. You have (1)a real leakage
    problem out on the distribution wiring, (2)
    a leaky appliance plugged into an outlet or
    (3) a flaky GFI.
 
    Do you have more than one GFI in the panel? If
    so, try moving the hot/neutral pair on the problem
    circuit over to another GFI. If the tripping moves
    to the new breaker, then downstream leaking is
    indicated.  If the problem does not move, then
    the breaker has a problem.
 
    Similarly, a wall-receptacle GFI can be used as
     
   a test tool. You can wire your 'problem feeder'
   to the LOAD pair of terminals while using a pair
   of jumpers from the LINE pair to the panel ground
   and any handy breaker. See if the test GFI complains
   about feeder quality.
 
   Incidentally, a GFI does not need the safety
   ground wire to function as intended. It measures
   DIFFERENCE currents in the hot/neutral pair . . .
   the leakage MIGHT be flowing back on the safety
   ground wire . . . or to another current sink . . .
   it doesn't matter.
 
   Many appliances like hair dryers and pressure
   washers have GFIs built right into the plug on
   the end of the cord.
 
  [img]cid:.2[/img]
 
   Note that many end-of-cord GFIs don't feature a third prong
   for safety ground . . . it's not needed to monitor and
   react to an IMBALANCE of current flow on the hot/neutral
   pair.
 
   There are other experiments that you can use to explore
   leakage on the problem feeder . . . but confirming
   proper operation of the panel GFI is the first . . .
 
    
    
 
  
  
    Bob . . .
 
  |  | - The Matronics AeroElectric-List Email Forum - |  |   |  Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:
 
  http://www.matronics.com/Navigator?AeroElectric-List |  
  |  
 
 
 
  
	
  
	 
	
	
		
	 
	
		|  Description: | 
		
			
		 | 
	 
	
		|  Filesize: | 
		 49.33 KB | 
	 
	
		|  Viewed: | 
		 4433 Time(s) | 
	 
	
		
  
 
  | 
	 
	 
	 
	 
	
	
		
	 
	
		|  Description: | 
		
			
		 | 
	 
	
		|  Filesize: | 
		 51.83 KB | 
	 
	
		|  Viewed: | 
		 4433 Time(s) | 
	 
	
		
  
 
  | 
	 
	 
	 
	 
	
	
		
	 
	
		|  Description: | 
		
			
		 | 
	 
	
		|  Filesize: | 
		 108.14 KB | 
	 
	
		|  Viewed: | 
		 4433 Time(s) | 
	 
	
		
  
 
  | 
	 
	 
	 
 | 
			 
		  | 
	 
	
		| Back to top | 
		 | 
	 
	
		  | 
	 
	
		jonlaury
 
 
  Joined: 06 Nov 2006 Posts: 336
 
  | 
		
			
				 Posted: Tue Sep 19, 2017 10:01 am    Post subject: Re: GFCI Breaker keeps tripping (Non   Aviation) | 
				     | 
			 
			
				
  | 
			 
			
				 	  | nuckolls.bob(at)aeroelect wrote: | 	 		  At 06:39 PM 9/17/2017, you wrote:
  
 
    ...Similarly, a wall-receptacle GFI can be used as
    
   ...a test tool. You can wire your 'problem feeder'
   to the LOAD pair of terminals while using a pair
   of jumpers from the LINE pair to the panel ground
   and any handy breaker. See if the test GFI complains
   about feeder quality...
 
   
  
    Bob . . . | 	  
 
 Is this correct?? Sounds like using a pair of jumpers from LINE pair to the panel ground is going to make a lot of sparks and smoke.
 
 2nd Question:
 In using a clamp on meter as depicted, assuming it can detect 5ma leak, will the meter show an absolute number? or will it show a positive value for leakage on the hot leg and a negative value for the neutral leg?
 That would be convenient   
 
 John
 
  |  | - The Matronics AeroElectric-List Email Forum - |  |   |  Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:
 
  http://www.matronics.com/Navigator?AeroElectric-List |  
  |  
 
 
 
  
 | 
			 
		  | 
	 
	
		| Back to top | 
		 | 
	 
	
		  | 
	 
	
		nuckolls.bob(at)aeroelect Guest
 
 
 
 
 
  | 
		
			
				 Posted: Tue Sep 19, 2017 1:23 pm    Post subject: GFCI Breaker keeps tripping (Non   Aviation) | 
				     | 
			 
			
				
  | 
			 
			
				At 02:52 PM 9/19/2017, you wrote:
 
  
   	  | Quote: | 	 		  On Tue, Sep 19, 2017 at 1:01 PM, jonlaury <jonlaury(at)impulse.net (jonlaury(at)impulse.net)> wrote:
    --> AeroElectric-List message posted by: "jonlaury" <jonlaury(at)impulse.net (jonlaury(at)impulse.net)>
  
  
   nuckolls.bob(at)aeroelect wrote:
   > At 06:39 PM 9/17/2017, you wrote:
   >
   >
   >Â  Â  ...Similarly, a wall-receptacle GFI can be used as
   >
   >Â  Â ...a test tool. You can wire your 'problem feeder'
   >Â  Â to the LOAD pair of terminals while using a pair
   >Â  Â of jumpers from the LINE pair to the panel ground
   >Â  Â and any handy breaker. See if the test GFI complains
   >Â  Â about feeder quality...
   . .
 
  
   Is this correct?? Sounds like using a pair of jumpers from LINE pair
   to the panel ground is going to make a lot of sparks and smoke. | 	   
    Perhaps my description was unclear . . . Let's
    try again. GFIs come in a variety of flavors not
    the least of which is the NEMA wall outlets with
    built in GFI. These outlets have TWO sets of terminals:
    (1) a line/neutral pair that faces the distribution
    box and (2) a line/neutral pair that can drive a downstream
    load with the added benefit of GF protection.
 
    You can wire one of these devices to operate not unlike
    the GFI fitted to the end of an appliance cord. A l/n
    pair of wires connects to any  handy breaker/ground
    in the distribution box. The Romex to be investigated
    connects to the l/n load terminals of the outlet.
 
    One could salvage a GFI cord of a hair dryer
    (thrift stores are have 'em for a few bux). Cut
    it at the dryer-end, strip back and add some alligator
    clips.
 
    Now you have a test tool that can plug into any
    120vac source and clip to a feeder under investigation.
    This too, like the suggestion above, simply adds a
    'real' GFI in series with the feeder under study.
 
    There is a caveat for using this methodology
    to find ground fault issues (milliamperes),
    suppose the breaker is tripping for reasons
    of hard faults (hundreds of amps). If I were
    to built a GFI test tool from a salavaged heater
    cord, I think I would put fuse holders in series
    with the alligator clips and populate them with
    1 amp fuses.  I do the same thing with my 'suicide
    cords': short line cords with that let me
    clip 120 vac to various articles under test. 
 
    Both of these tests simply substitute a known-good
    GFI for the nuisance tripping GFI to see if
    the fault is in the wiring (test GFI trips too) or
    in the panel GFI (test GFI stays closed).
 
  
   	  | Quote: | 	 		    2nd Question:
   In using a clamp on meter as depicted, assuming it can detect 5ma leak, will the meter show an absolute number? or will it show a positive value for leakage on the hot leg and a negative value for the neutral leg?
   That would be convenient   | 	   
    There is no 'polarity' to an AC measurement so
    yes, a sensitive, clamp-on ammeter would only
    display absolute value of the imbalance.
 
  
 
  
    Bob . . .
 
  |  | - The Matronics AeroElectric-List Email Forum - |  |   |  Use the List Feature Navigator to browse the many List utilities available such as the Email Subscriptions page, Archive Search & Download, 7-Day Browse, Chat, FAQ, Photoshare, and much more:
 
  http://www.matronics.com/Navigator?AeroElectric-List |  
  |  
 
 
 
  
 | 
			 
		  | 
	 
	
		| Back to top | 
		 | 
	 
	
		  | 
	 
	
		 | 
	 
 
  
	 
	    
	   | 
	